Gas meter u6
54 metres from the house
AECV at rear outside with no test point
possibly 1" iron from meter
range cooker and boiler should be 42 kw
gas rated and got 37 kw
rang GSR enough said.
what would you do?
It's a graveyard, there is absolutely no straight run,the 54 metres would finish up 100metres trying to go round all the graves, I've no idea which direction the iron that is already there goes in.
What about moleing it?
It's not cheap, but, on a site I was on in York afew weeks ago they moled a 64 mm water and 50mm gas ( about 30m) this was yo go under a cobble street. They dug holes at each end and had the pipe in in a couple of hours.
Can you imagine the mole popping out of the hole accompanied by bits of arm, leg, skulls or someone needs to dig up or open an existing grave and my brand new 42mm goes straight through the rib cage.
Gas meter u6
54 metres from the house
AECV at rear outside with no test point
possibly 1" iron from meter
range cooker and boiler should be 42 kw
gas rated and got 37 kw
rang GSR enough said.
what would you do?
Its only going to provide about 2 metres cubed/hour on this run with a 1 mbar working pressure drop from end to end. Hang the boiler on a head stone or put a bigger pipe in.