Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Setting Expansion Vessel in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
P

Paul Turton

Hi looking for a bit off advice.

Doing a commercial premises.Closed system for the heating.Ive set the press unit at 1.2 but not too sure about the expansion vessel?

Also a booster set for the cold mains which is set at 1.5 bar with a remote expansion vessel.What should this be set too as well.

Any help would be much appreciated compared to the no help from heating engineer today.

Cheers for any advice given.
 
"Any help would be much appreciated compared to the no help from heating engineer today."

what does that mean your not a/the heating eng???????
 
It means im a gas qualified engineer but have never set up a commercial installation expansion vessel before and needing too do it for the commisioning process.
 
Last edited by a moderator:
it should come pre set esp if you have sized it right

should be a data plate somwhere
 
90% of the design pressure.

Which is 1.08 bar but I'd set it at 1.1bar.

Don't forget that this would be on an empty system.
 
And the booster set you'll need to adjust on site. Increase the vessel pressure until you get no more pump bounce.
 
Is that the same for both vessels Croppie or only the Heating one?

Just wondering because the booster set is set at 1.5.

Cheers
 
It's been a long time since I last set up a booster set Paul. Suck it and see really. Start at 1.5 bar, some need more, some less. You'll know when you get it right because the pump won't bounce when it comes up to pressure.
 
Status
Not open for further replies.

Similar plumbing topics

it is brand new ( 6 months old ) Worcester gas...
Replies
2
Views
682
losing pressure
L
Pin hole leak on suction side of pump.
Replies
1
Views
467
Start it again in the gas safe only forum and...
Replies
2
Views
817
  • Question
.2 below let’s say your cold pressure is 1.5...
Replies
3
Views
1K
Back
Top