Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Shock arrestor on cold water pressurising hot water? in the Bathroom Advice area at Plumbers Forums

Messages
3
Hi all, new here. Spark, not a plumber.

I have a question about something at my house that's puzzling me.

Combi boiler system in a terraced house. I've had water hammer/water shock whenever something is turned off quickly, mainly the washer. I fitted a PRV just after the stopcock and reduced the incoming pressure to around 2 bars which stopped the problem but the shower (mixer shower running from the boiler) was terrible at this pressure so upped it 3 bar. Hammer/shock returns but not as bad.

Bought a shock arrestor (Altechnic diaphragm type) and fitted it just before the washer. Happy days it's cured the hammer when the washer/toilet valves shut off. Problem is when a cold water valve or tap is opened anywhere in the house there's hammer/shock coming from the hot tap side now this is when something is opened on the cold side, not shut off. Puzzled me how this is possible? Is the shock arrestor pressurising the hot water by back feeding through the boiler!?

Any ideas or help would be much appreciated.

For info the incoming pressure is 3.5 bars. It's been reduced to 3 bars now by the PRV valve. The arrestor is pre-charged at 3.5 bars.
 
Arrestor needs to be fitted before boiler / cold feed to the boiler should sort you out
 
When you say hammer is this an on going banging or just one thump when you open something

It's just a one off thud/shock, it's not the multiple hammering you sometimes get with older houses.

Arrestor needs to be fitted before boiler / cold feed to the boiler should sort you out

That would make sense I'll try putting it before the boiler.

Thanks for the replies.
 
Update: Removed the shock arrestor from the washing machine pipe and fitted it to the cold water feed to the boiler. This stopped the symptoms mentioned in the original post but started the Thud/shock when the washer/toilet was shutting off again.

I've completely removed the shock arrestor as it seemed to be causing more issues than it was solving. I've turned the washer and toilet isolators to half way and this has solved the issue of the hammer/thud/shock in the pipes.

Thanks for all the suggestions and replies.
 

Similar plumbing topics

  • Question
I would of clipped the pipework but it is...
Replies
2
Views
304
  • Question
Thanks for the tip. I have an outside tap so...
Replies
7
Views
452
C
  • Question
Is there a ball valve on the flexihoses? Might...
Replies
1
Views
897
Probably your main stopcock is not fitted the...
Replies
1
Views
565
  • Question
Definitely worth checking the clipping...
Replies
1
Views
687
Back
Top