Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss shower smells of fish in the Showers and Wetrooms Advice area at Plumbers Forums

phil hair

Gas Engineer
Messages
42
i have noticed recently a faint fishy smell coming from bath while i am showering.
(**********ok enough of that fellers****************)

its an electric shower, used everyday, so doubt it stagnant water, any ideas?
 
the wiring in the pull cord switch thingy has charred. the wire from the circuit breaker to the switch. charred back about 1 inch. ive not checked yet if it was because of a lose connection. would it be ok to cut back the wire past the charring, and reconnect it to the switch/new switch, or does the whole wire need replacing?

thanks again.
 
Upvote 0
What power is the shower?
What size is the cable?
What rating breaker (MCB) is it on?
 
Upvote 0
8.5kw
6mm? not sure how to measure this, but its bigger than socket t/e but not huge
40 breaker

If you can see enough of the cable, the size will be moulded into the sheathing.

The cable is likely inadequate. 6mm can carry up to 47A if clipped to an open wall. As soon as you run it through trunking or within a stud wall the load capacity drops. Even more so if the cavity is insulated - to as little as 34A. Your shower will draw almost 39A.

I would strongly advise getting a sparky in to assess the cable run and would certainly look to uprating it to 10mm2.
 
Upvote 0
Cable definitely undersized, typically shower has been replaced with a more powerful one
Rules of thumb 8.5kw -= 36A so need 40A MCB and min 10mm2 cable and new 40A double pole pull cord switch located in the correct place - there are regulations might need RCD/RCBO
- You need to get a qualified sparks in to check above and run new cable from CU
 
Upvote 0

Similar plumbing topics

  • Question
Is the main drain vented? Sounds like the...
Replies
1
Views
601
  • Question
Could you post a picture of the shower trap...
Replies
2
Views
686
  • Question
Sounds like a syphoning problem in the main...
Replies
3
Views
464
  • Question
Hi, It does look intact but a little the worse...
Replies
4
Views
772
T
  • Question
For about a year, my shower on a third floor...
Replies
0
Views
580
Timmy1
T
Back
Top