marshr02
Looking for advice - probably thinking about it too much. Have 1.8m of 50mm pipe from internal stack running at 20mm/m alongside joists - then swept bend to bring it through floor alongside shower tray. Then there is a 50mm swept T for rodding if required solvent welded as tight as possible to the swept bend coming from below. A 50-40mm reducer in the 50mm T gives the 40mm connection running just shy of 1m @ 25mm/m to the shower tray. The step up from finished floor to tray top is 140mm. Obviously according to paper (18-90mm/m) this is all tickety boo - but I have the option of shoving 18mm ply under shower tray to raise the whole lot 18mm to give a better slope on the 50mm pipe - would this be sensible OR is the current arrangement ok? Seems to me that 18mm/m is an absolute limit which means on site 25mm/m is a more realistic bottom slope to aim for to cope with any floor movement or inaccuracies at 1st fix?