I was out looking at a job the customer wants a rad moved. Turns out he needs 2 rads repiped & a new shower room & all in solid floors in a fairly new posh flat.
I am not gas qualified, but first thing I was asked about was the combi gas boiler wasn't working. Quick look at the boiler showed no pressure on the gauge & a seperate expansion vessel fitted below it in a cupboard. Turns out they have had it serviced by a gas guy & he said the boiler vessel had been replaced to an external vessel by a previous engineer. He had apparently refilled the system to correct pressure but it had now dropped to zero.
I went to refill the boiler and first second I looked at it I realised why the customer wasn't able to do it. A isolating valve (cheap ballofix type) was fitted on the heating side & turned off! Expansion vessel & filling loop therefore not linked to system.
So the engineer who installed the new expansion vessel had obviously not been clever & isolated the vessel with a valve & the service guy came out, replaced & worked on the filling loop & refilled system by turning the valve on & off! I really should get my gas certificate, if that's the quality out there.
I am not gas qualified, but first thing I was asked about was the combi gas boiler wasn't working. Quick look at the boiler showed no pressure on the gauge & a seperate expansion vessel fitted below it in a cupboard. Turns out they have had it serviced by a gas guy & he said the boiler vessel had been replaced to an external vessel by a previous engineer. He had apparently refilled the system to correct pressure but it had now dropped to zero.
I went to refill the boiler and first second I looked at it I realised why the customer wasn't able to do it. A isolating valve (cheap ballofix type) was fitted on the heating side & turned off! Expansion vessel & filling loop therefore not linked to system.
So the engineer who installed the new expansion vessel had obviously not been clever & isolated the vessel with a valve & the service guy came out, replaced & worked on the filling loop & refilled system by turning the valve on & off! I really should get my gas certificate, if that's the quality out there.