Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Soil pipe for toilet frame help in the Boilers area at Plumbers Forums

Messages
9
Hi all
I am trying to fit a toilet frame in my bathroom, I have an issue whereby the soil pipe out of the frame does not line up with the pipe in my house, the pipe is about 70mm higher.
See picture for details, how is it best to do this ? Do they do an offset adapter for around 70mm?
Cheers

CC3C6D31-BCED-4003-A6F4-6A90F2D59618.jpeg
 
is the soil pipe push fit or glued?
 
Your easiest option is 2x 135° bends pushed together. If it's slightly more than what's required just raise the height of the toilet frame to suite.
 
This is one
https://www.NoLinkingToThis/p/floplast-sp435-135-bottom-offset-bend-black-110mm/44403
You will need two of them to push together to form the offset you need.
 
This is one
https://www.NoLinkingToThis/p/floplast-sp435-135-bottom-offset-bend-black-110mm/44403
You will need two of them to push together to form the offset you need.
Won’t that be too much of an angle ?
Also, does one end just push fit around the soil pipe and the other end push fits to the pipe that joins to the frame ?
 
I don't know if it's it's too much of an angle of not. You certainly won't be able to buy a fitting that will fit perfectly. It's trial and error. The good thing about those frames is You can raise the waste height if required or pull the frame out further and just increase the size of your boxing. What adaptor was supplied with the frame to fit the 110mm pipe?
 
I don't know if it's it's too much of an angle of not. You certainly won't be able to buy a fitting that will fit perfectly. It's trial and error. The good thing about those frames is You can raise the waste height if required or pull the frame out further and just increase the size of your boxing. What adaptor was supplied with the frame to fit the 110mm pipe?
The pipe that came with the frame was 90mm, there is an adapter that fits into the same size as the soil pipe
 
The adaptor is probably pushfit so you'll need 1 of these instead
https://www.NoLinkingToThis/p/floplast-sp163-135-bend-single-socket-black-110mm/63147
And one of these
https://www.NoLinkingToThis/p/floplast-sp440-135-top-offset-bend-black/88027
 
I usually use the drainage stuff instead, they do more variety of bends such as 15 & 30 degrees. Can be useful when a 45 is too much. As it's not on show it doesn't matter.

https://www.NoLinkingToThis/c/heati...category=cat831514&page_size=20&page_start=20

As others have said, the adaptor that comes with the frame will be push fit so ensure it goes into a pushfit socket and not glued.

You may be as well removing the white pipe from the soil junction and renewing from there with new 4 inch and the required offsets.
 
I usually use the drainage stuff instead, they do more variety of bends such as 15 & 30 degrees. Can be useful when a 45 is too much. As it's not on show it doesn't matter.

https://www.NoLinkingToThis/c/heati...category=cat831514&page_size=20&page_start=20

As others have said, the adaptor that comes with the frame will be push fit so ensure it goes into a pushfit socket and not glued.

You may be as well removing the white pipe from the soil junction and renewing from there with new 4 inch and the required offsets.

That’s underground mate can’t use them
 
I can't see any issue either? It's not external.

All I can think of is the BS numbers, as to which if I'm not mistaken Soil and underground waste are made to the same specification. Correct me if i'm wrong.
 
The brown / orange underground soil has no uv protection so it must be buried or kept in complete darkness

White, black and grey soils do.

Would probably be okay, just a bit unsightly eh?

Those are the fittings that come with the frame,

check the connection on the wall hung pan it might be the same as a normal flexi pan-con
 
Don't use a flexi and bury it in the tiled frame box - do it properly with rigid soil pipe. We've done all this before on another thread if you care to look. Suffice to say a Marley two-part solvent weld adjustable bend is the kiddy to get you out of trouble. (Have to go to a proper plumber merchant you will not find it in B & Poo or Poofix etc.)
 

Similar plumbing topics

Thanks Shaun and Last Plumber. I checked the...
Replies
3
Views
443
B
I wouldn't bother even trying. Water jetters...
Replies
1
Views
449
10 o’clock / 45 degrees would be better than...
Replies
3
Views
577
Thank you so much, that's very helpful!