Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss some boilers do 'ave 'em... in the Boilers area at Plumbers Forums

Status
Not open for further replies.

Jimbob

Gas Engineer
Messages
644
recently got called out to a myson floor standing natural draught boiler.

Very simple boilers so you would think them not to be much of a problem when it comes to troubleshooting. When i first arrive the burner would not light, despite there being a nice steady pilot. So i test everything down to the gas valve and all was fine, thermostat functioned, thermocouple workes fine holding open the pilot and i was getting 230v to the gas valve.

So i replaced the gas valve thinking sorted... but no. Still no burner ignition despite there being 230 at the valve, and even the burner pressure getting upto 19.5mbar as specified. So i cleaned the burner and the injector, still no flame. What am i missing?

im starting to think it could be down to a blockage in gas pipe, i suppose i could test for this by letting the gas valve open and doing a gas rate. Surely cant be it though
 
Is the 19.5mb the burner pressure or gas valve inlet pressure?

If you are getting 240 at the gas valve, and then 19.5mb at the burner pressure point, theres got to be a blockage somewhere
 
Last edited by a moderator:
19.5 burner pressure. Really can't get my head round it as burner looks fine and so does the injector. Got a friend with a bit more breakdown experience to go have a look at it.
 
Check if there's 240v neutral to earth, if so you've got a broken neutral
 
Status
Not open for further replies.

Similar plumbing topics

PH is 7.5. Chloride is 194. The last water...
Replies
2
Views
648
The boiler is just responding by limiting the...
Replies
8
Views
1K
I don’t know your boiler but would expect it...
Replies
3
Views
669
Ha, yes funny that. As with gas the rating of...
Replies
10
Views
1K
You'd have to have gas meter removed if you...
Replies
19
Views
2K
Back
Top