Hi Gents,

I'm currently doing a Job at a small warehouse where i've been fitting a Basin and toilet, the owner of the premises is a close friend of mines and has just recently taken over the premises.

The problem i've come across is, the radiators in this place are not warming up so well, practically luke warm!..

It is a large system comprimising of 14 Double convector Double panel radiators (Approx 700x1200) in size.

The system is no more then 2yrs old because we have some form of paper work, just no installer details.

There is a Vaillant Ecotec plus 937 installed, seen as there was 2 existing toilets and 1 kitchen.. Now i''ve added another basin and toilet.

The Hotwater side of the system is completely fine, just the heating.

So far i've gathered some info from Vaillant technical support (pretty poor technical staff), and have purchase a "VR40" which has allowed me to fit an External pump on the heating circuit.. I have fitted this and have not seen any differences what so ever!

So yestrday (Saturday afternoon) i have placed an order for a 23 litre expansion vessel and will be fitting this as obviously the standard vessel that is fitted inside the boiler cannot cope!

Will fitting this vessel on the Return side of the Heating circuit be beneficial??

I would be grateful if anyone can tell me, if what i'm about to carry out is the next best thing to do??

Thanks guys!
 
What makes you think that there's a problem with the expansion vessel?
 
Ecowarm - The water in the system is very clean, it can be deemed as drinking water from what i've seen.

Shorticus - Im adding another vessel because there is only soo much a the vessel in a 937 combi can cope with, True or not, please fill me in ??
 
A large system may need a larger expansion vessel than the one in the boiler
 
just checked the manual, the boiler's got a 10l expansion vesel that's good for a 100l system, do you think that the system's larger than that?
 
Definitely more then a 100litre system mate, cos the flow & return pipe lines from boiler to the last radiator is atleast 23metres from the top of my mind
 
Definitely more then a 100litre system mate, cos the flow & return pipe lines from boiler to the last radiator is atleast 23metres from the top of my mind

just out of curiosity, has the prv discharged?
 
The size of the expansion vessel isn't the reason it isn't heating the space. The problem is that the boiler is spec'd out at 28kW for CH. Thats a load for that boiler in a domestic app let alone a wharehouse.
 
The size of the expansion vessel isn't the reason it isn't heating the space. The problem is that the boiler is spec'd out at 28kW for CH. Thats a load for that boiler in a domestic app let alone a wharehouse.

I was pondering that too, those rads have got to be say 2kw each + pipe loss etc etc
 
one other thing to have a quick check on is the internal auto by-pass, could possibly have a bit of debris on the seat
 
The size of the expansion vessel isn't the reason it isn't heating the space. The problem is that the boiler is spec'd out at 28kW for CH. Thats a load for that boiler in a domestic app let alone a wharehouse.

That's the 1st thing that came to my mind, but seen as it is a big job and quiet pricey to replace, maybe some essential add-ons may help! :-S
 
I havent seen any water triccle out but it does tend to loose little pressure every few days, with no signs of leak on pipe work, so assuming it is the PRV

then you're probably right about needing extra space for expansion, not sure it'll cure the heating issue though
 
one other thing to have a quick check on is the internal auto by-pass, could possibly have a bit of debris on the seat

Could give it a go, but doubt very much as it doesnt look like a very old installation with minimal use!
 
Could give it a go, but doubt very much as it doesnt look like a very old installation with minimal use!

worth a look just to eliminate it, someone on here last week had a bypass problem so it can occur from time to time.
Make sure you let us know how you get on Hary-j, good luck with it mate
 
So what you reccan gents??, time for a replacement to a vaillant ecotec 46kw or 65kw??

Really don't wanna have to tell my mate this :-(, so if i can cure it more better!
 
looks like a shortfall , 28kw output on boiler and a load of 35kw on rads
 
Status
Not open for further replies.

Similar plumbing topics

1/4 turn black knob on both. open bleed screw...
Replies
7
Views
932
S
No point in doing anything with the radiators...
Replies
1
Views
894
I plan to remove 8+. I guess the fact remains...
Replies
2
Views
906
  • Question
Correct. Bleed from bottom up to allow air...
Replies
3
Views
1K
    • Like
From this post, I think you’ve got a good...
2
Replies
47
Views
6K
Back
Top