Hey I've heard a straight swap electric shower is un-notable to the electric regs. Does this just require the shower to be of the same power i.e, 8.5 kw.
 
Not necessarily.
If you take a 10.5 kw out you cant just wack a replacement In without knowing the supply cable is adequate. The previous installer may have been a diy guy and potentially fit it on 6mm cable whih would overheat and become a fire risk.

You need to be competent to do electrical safety checks. Do unless your on an electrical competent persons scheme you could come unstuck
 