Strange greenstar 28i junior fault | Plumbing Jobs | The Job-board | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Strange greenstar 28i junior fault in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

zeebeedee

Plumbers Arms member
Plumber
Gas Engineer
Messages
3,143
Customer complaining heating would only stay on for 10 mins. Boiler fired for ht/hw and worked fine. Pressure would rise to over 2 bar and the burner would knock itself off. No lockout.

Thermistors in range. Expansion vessel ok and flexi connecting it. Pump ok.

Heres the strange part , the boiler wouldn't attempt to fire for ht/hw again until the pressure dropped.

Im im convinced its overheating due to a internal blockage. Back tomorrow for a flush.

Anyone seen this before?
 
Can you run it with the sensors out of there pockets to test?
 
These don't have a water pressure switch so must be a circulation problem I would say? Not wildly over gassed is it?
 
What's your thinking there?

With the sensors not being able to "sense" you'll be able to see of it carries on firing. If it gets mad hot hot it'll make some horrible noises, so blockage. If it fires and runs sweet, it's the señsor/sensors.
 
Status
Not open for further replies.

Similar plumbing topics

If you have the right temperature rise for the...
Replies
10
Views
3K
Have you checked L-N ? 240 ?
Replies
1
Views
2K
Thanks very much for your help.
Replies
4
Views
1K
Hello All- (Usual caveats apply: I am the...
Replies
0
Views
207
End to end test it would be my next port then...
Replies
3
Views
1K
Back
Top