Customer complaining heating would only stay on for 10 mins. Boiler fired for ht/hw and worked fine. Pressure would rise to over 2 bar and the burner would knock itself off. No lockout.
Thermistors in range. Expansion vessel ok and flexi connecting it. Pump ok.
Heres the strange part , the boiler wouldn't attempt to fire for ht/hw again until the pressure dropped.
Im im convinced its overheating due to a internal blockage. Back tomorrow for a flush.
Anyone seen this before?