been to do a landlord safety check on a boiler I look after an old ariston -it has a 1mb gas leak no smell of gas been like this for ages . went today for yearly check o find new boiler fitted free by major company - boiler only now(fire disconnected) on the gas supply and still the 1mb drop- since they fitted a new boiler they never cured the leak
 
Leave it as is, no further action required. Unless you want to give the landlord some grief!
 
Last edited:
Surely the rule is new appliance, being the only appliance in the house no drop is allowed. Get them back.
 
Surely the rule is new appliance, being the only appliance in the house no drop is allowed. Get them back.
i agree no drop permissible,if its a new boiler no drop allowed on carcass,and anyway if other appliances fitted once isolated there must be no drop
 
I/1b states that the drop must not increase on existing installation. It's existing and upon commencing the installation was compliant and therefore legal and acceptable to be the same way when they finished. But me personally I don't like any drop any of the time
 
Surely the rule is new appliance, being the only appliance in the house no drop is allowed. Get them back.

Yes the installer should have repaired, but as you go in its no smell and 1mbar drop. Pass as it's now an existing installation.
 
Yes the installer should have repaired, but as you go in its no smell and 1mbar drop. Pass as it's now an existing installation.

I agree mate ok now as it is . if I had done I would have found
 
Status
Not open for further replies.

Similar plumbing topics

We've just sorted one of these situations...
Replies
9
Views
1K
Don’t know if this is the right part but...
Replies
1
Views
556
Fits back on flue on top of boiler
Replies
3
Views
658
I mean you can test with a multi meter on the...
Replies
9
Views
803
Back
Top