mike_s
If I moved into a house with a good stored hot water system I'd never rip it out for a combi unless I was desperate for space.
Combi's cost more to run, there's more to go wrong and generally you can only have one hot tap on at a time.
In a couple of weeks I'm doing a 300 litre unvented with 40kw heat only boiler in a large house, external expansion vessel on the heating.
It took them months to agree to the job as the customers dad had told them their Worcester highflow was great.
So I calculated that if you use a 40kw highflow for 2 hours a day that will cost around £1000 per year on hot water alone. The unvented cylinder would cost around £80 per year on the hot water if you have 2 baths or showers a day plus an hour washing up or about £125 if you have 3 baths/showers per day.
That sold the job as the extra grand in installation costs of the cylinder would be payed for in a year.
Even in small houses, combi's are often inefficient and inconvenient. All you need is a cylinder that is big enough so you arn't running out of hot water all the time.
Combi's sound like a good idea to many but I point out why they arn't. I've got 4 boilers to install in July, only one is a combi and that's a swap.
Builders are another culprit of the combi culture as they hardly build airing cupboards any more.
Another customer from America chose me for their job as I was the only one who didn't reccomend a combi, she had never seen a combi before coming to Europe and thought they sounded inefficient. They had a large house with a whole room just for the cylinder, perfect.
A customer today with an Ideal Mexico 2 said to me today "British Gas said I want a combi"
I said "Why? Do you run out of hot water all the time? Are your tanks not high enough, do you need the space?
The answer was "No, shower is great it works off the cylinder with good pressure as the tank is high, never ran out of hot water, my wife loves the airing cupboard, I just thought everyone gets combi's these days"
It winds me up, especially British Gas ripping out perfectly good S and Y plans for Worecester 24i Junior's in 4 bed houses.
Customers needs to be educated on what is best for them.
Combi's cost more to run, there's more to go wrong and generally you can only have one hot tap on at a time.
In a couple of weeks I'm doing a 300 litre unvented with 40kw heat only boiler in a large house, external expansion vessel on the heating.
It took them months to agree to the job as the customers dad had told them their Worcester highflow was great.
So I calculated that if you use a 40kw highflow for 2 hours a day that will cost around £1000 per year on hot water alone. The unvented cylinder would cost around £80 per year on the hot water if you have 2 baths or showers a day plus an hour washing up or about £125 if you have 3 baths/showers per day.
That sold the job as the extra grand in installation costs of the cylinder would be payed for in a year.
Even in small houses, combi's are often inefficient and inconvenient. All you need is a cylinder that is big enough so you arn't running out of hot water all the time.
Combi's sound like a good idea to many but I point out why they arn't. I've got 4 boilers to install in July, only one is a combi and that's a swap.
Builders are another culprit of the combi culture as they hardly build airing cupboards any more.
Another customer from America chose me for their job as I was the only one who didn't reccomend a combi, she had never seen a combi before coming to Europe and thought they sounded inefficient. They had a large house with a whole room just for the cylinder, perfect.
A customer today with an Ideal Mexico 2 said to me today "British Gas said I want a combi"
I said "Why? Do you run out of hot water all the time? Are your tanks not high enough, do you need the space?
The answer was "No, shower is great it works off the cylinder with good pressure as the tank is high, never ran out of hot water, my wife loves the airing cupboard, I just thought everyone gets combi's these days"
It winds me up, especially British Gas ripping out perfectly good S and Y plans for Worecester 24i Junior's in 4 bed houses.
Customers needs to be educated on what is best for them.