I have a quick question

The air pressure in the expansion tank of a new combi boiler is preset for 1.5bar.
I filled the system with water up to 2bar.

My question is, what will be the correct air pressure in the tank now after I filled the system with water? should it be 1.5bar or should it be higher?

Thanks sasi
 
It should tell you in the installation instructions. It depends a bit on the height of the house and the relative position of the boiler but I generally set the ones I install to about 1 bar.
 
Hi grahamep

Thanks for your reply, maybe I should make my question moor clear. the air pressure and the water pressure are all set as they should,no problem there.
All I want to know is if you took a reading of the air pressure when the system is running will it register higher then the preset pressure. It is not a question of right are wrong, I just want to know if the air pressure in the vassell increase.

Thanks sasi
 
The pressure will equalise either side of the diaphragm so the pressure in the vessel would read the same as the system pressure gauge.

Mike
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
It could well be, the OP will soon hopefully...
2
Replies
35
Views
2K
  • Question
Before doing this, check the level in the cold...
Replies
9
Views
1K
  • Question
Red circles show my new AAVs and the manual...
Replies
17
Views
2K
  • Question
Ya, they said the fact the anti-vibration...
Replies
6
Views
707
  • Question
It could be best to get him back to have a look
Replies
24
Views
2K
Back
Top