Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Thermal Store cylinder noisy in the UK Plumbers Forums area at Plumbers Forums

Messages
4
Hi all,

I moved to my flat 3 years ago and I noticed since then than the hot water thermal store cylinder is noisy (kettle noise) when the heating element is on (around 2 hours a day during economy 7 hours)
This wasn't a problem before since it is located far from the main bedroom but now, we have a baby and his room will be close to the cabinet where the thermal store cylinder is located.

Thermal Store cylinder details:
  • Telford copper cylinder tristor 210 litres. I guess from where the flat was build early 2000.
  • has 2 heat elements (3kw each). 1 connected to economy 7 and the other one connected to high tariff for boots porpuse.

Is there a way to reduce the noise of the thermal store cylinder? i.e. adding something to the thermal liquid.

Thanks

Andres
 
One option is to replace the economy 7 immersion with a "low watt density" version. Not necessarily lower power, but the idea is to have a bigger surface area of element in contact with the water, and at a lower temperature, which is supposed to reduce the 'kettling' noise.

If you find something to put in the thermal store water, I would check with Telford they would be happy with you using it.
 
Loud kettling can be caused by limescale build up, if you live in a hard water area then maybe just changing the element will cure the problem as normal element heating noise is (in my case anyway) hardly noticeable.
 
Loud kettling can be caused by limescale build up, if you live in a hard water area then maybe just changing the element will cure the problem as normal element heating noise is (in my case anyway) hardly noticeable.
Thanks for the reply.
I think the thermal store cylinders does not suffer from limescale issues since always uses the same water (or liquid, not sure what is inside) in the cylinder to store the heat, but correct if I am wrong.
I do live in a hard water location.
Thanks
 
One option is to replace the economy 7 immersion with a "low watt density" version. Not necessarily lower power, but the idea is to have a bigger surface area of element in contact with the water, and at a lower temperature, which is supposed to reduce the 'kettling' noise.

If you find something to put in the thermal store water, I would check with Telford they would be happy with you using it.
Thanks for the reply, I will check this option but first i need to know what type of heating elements the Thermal Store cylinder has.
Would I need to empty the cylinder to replace the heating elements?
Thanks
 
The immersion is 14” 3kw with a 2 1⁄4” boss. The manufacturers replacement is part no. SHELINK14TRI, which maybe is what you still currently have. Just replacing it would probably make it a bit quieter for a while. You would need to drain the tank to do that, and when topping it up should add the liquid inhibitor that's supposed to be there.
It's only the lower element that would be making noise at night. Don't need to do the upper one unless there is a noise problem on boost (if you use it).

As an example, there is a "low watt density" equivalent immersion here: 14" - XT Maxistore Low Watts Density Domestic Immersion Heater - 3KW - XT209 - https://www.advancedwater.co.uk/prod-232-255-1406.html
Would be wise to check with the cylinder manufacturer - they might have a preferred alternative.
 

Similar plumbing topics

  • Question
Yours is an old fotic cylinder, Thermal store...
Replies
1
Views
978
  • Question
Yes, The size of the external expansion...
Replies
17
Views
10K
Z
  • Locked
get another plumber to check it over, could be...
Replies
1
Views
2K
lame plumber
L
C
  • Locked
  • Question
An unvented will give you the best possible...
Replies
9
Views
2K
Plumb Ugly
P
Back
Top