i have to fit thermostatic mixer valves on to childrens basins in a nuserary problem is the hot water is from a fortic wih only a few feet of head and the cold is mains preasure so get no mix due to preasure differnce suggestions on a post card please
 
Hi Steve,

This is going to cause you a headache mate.

I would phone a couple of valve makers and see if a pressure reducing valve can be fitted to the cold mains, as not to disrupt the operation of the valve. Check what pressure you have at the hot. Will crap no doubt.

As its a fortic, im assuming there is hardly any room to fit a CWSC??

eas
 
You could put a pump on the hot, and reduce the pressure on the cold to try & match it ?
 
Could a pressure equailising valve work? Or would there not be sufficient pressure behind the hot?
 
just had a thought about this and want to run it by everyone how about if i put a tank con into the tank of the fortic to provide equal preasure cold to mixer
my first thought was the tank isnt big enouch but then i realised its only supplying the same amount of water be it ,just hot or mixed any thought much appreciated

just had a thought about this and want to run it by everyone how about if i put a tank con into the tank of the fortic to provide equal preasure cold to mixer
my first thought was the tank isnt big enouch but then i realised its only supplying the same amount of water be it ,just hot or mixed any thought much appreciated
anyone got any thoughts on this i realy need to provide a solution tommrrow
 
Last edited:
If you fitted a tank connector to the fortic, even though its a cold supply the connector would have to be just above where the hot water is (bottom of CWSC part of fortic), thus would come out luke warm, rather than cold? Although i suppose the mixer would compensate this and mix accordingly. Maybe im just talking rubbish.
Also (just thinking) what if the cylinder stat suddenly failed and the hot boiling water expands into tank?
 
Last edited by a moderator:
if you fitted a tank connector to the fortic, even though its a cold supply the connector would have to be just above where the hot water is (bottom of cwsc part of fortic), thus would come out luke warm, rather than cold? Although i suppose the mixer would compensate this and mix accordingly. Maybe im just talking rubbish.
thats true they do get warm maybe a fe and e tank might be a beter option? ALTHOUGH ITHE STAT WOULD BE SET LOW
 
Last edited:
How many basins are there ?
Is fortic cylinder in question feeding any other hot outlets in nursary ?
Is the mains pressure good,giving good fill time to tank ?
Is cylinder heated by immersion or boiler ?
 
Last edited by a moderator:
If the stat is set low (i assume you mean on the immersion heater or cylinder stat) wouldnt there be risk of legionella?
 
How many basins are there ?
Is fortic cylinder in question feeding any other hot outlets in nursary ?
Is the mains pressure good,giving good fill time to tank ?
Is cylinder heated by immersion or boiler ?
imersion great main and six minature basins used soley for hand wash
 
Some TMVs can handle unbalanced pressure, others can't. Some are suitable for gravity, others aren't.

I think the Altechnic Caleffi ones are suitable for your application but you will have to check the specs. You may need to fit a pressure reducer to the cold side.

I have been fitting the Caleffi ones for the last year to new bathtubs where there is mains cold and hot gravity and all has been OK so far.
 
Status
Not open for further replies.

Similar plumbing topics

Have you got a photo of the sink at the...
Replies
2
Views
632
  • Question
Thankyou, I have already installed a hot and...
Replies
13
Views
1K
If it rises steadily while system heats up to...
Replies
5
Views
975
V
  • Question
As above, and did you check the suitability of...
Replies
2
Views
876
Deleted member 120897
D
  • Question
Thanks. I'll try to find a hard copy as I...
Replies
3
Views
951
Back
Top