I had some guy on saying that I should be fitting TMV's on cylinder outlets to reduce hot water temperatures down to 45 degrees C on leaving the cylinder. Apparently he fits his that way! Now I have been involved in legionella prevention in commercial and industrial systems for about 20 years and know that kind of thing is really risky. He mentioned G3 to me, then I quoted back word for word the requirements for blending valves on cylinder outlets heated by uncontrolled heat sources (stoves) is what that part is intended for, and the temperature must be (if I remember correctly without looking up, (correct me if I am wrong) 60 to 65 degrees C). TMVs should be located as close as possible to the taps (less than 1m). Then he tried to tell me that you couldnt fit any valves between the cylinder outlet and the taps!
It's scary what some people do! How many people are reading the Building Regualtions without actually understanding the requirements?