Done a llsc at a property today which had been done by a couple different engineers before.
Picked up some usual stuff along with an unsealed flue however upon a gas rate on a logic+ 30 kw i got 27 kw and 11mbar at aplliance.
I double checked with ideal and they said they would not recommend this an to upgrade pipework from 15 mm to 22mm.
Well noted this on cert and decided to AR it .1 , because of flue and 2, because of pipe issue.
Well it kicked right off with the landlord who decided to call gas safe who basically said i was wrong and then procededto scout right through all google listings to study my finding.
The cust asked how come its passed last 5 years and suddenly i have found this ?
The AR for the pipework was just as much because the install was a mess, so im basic querying what the collective would of done here?