Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Tiger 944 gas fire problems in the Gas Engineers Forum area at Plumbers Forums

Status
Not open for further replies.
B

Buller44

Hi ppl,

Been to a customers this afternoon who have been experiencing problems with a Tiger 944 nat gas fire (stove).
It has been shutting off between 25-45 mins of being lit.

I was at the property for about 45 mins today checking various things. (inlet gas pressure, spillage, flue flow, oxypilot seems clean) fire was working fine until i packed all my kit away and then all of a sudden it just went off.
My customer said that it seems to happen when the boiler fires for heating or when someone opens a hot water outlet in the kitchen. Could this be coincidence? When the fire is on max gas inlet is 19.8 mbar when i fired the boiler it went down to 15.9 mbar and then steadied at 17 mbar. There was no spillage from the fire so i assume that ventilation isn't the problem.
Please excuse my basic drawing skills :).

Grant.JPG

Any suggestions please?
 
Have you checked the gas pressure at meter with all appliances running?
 
Have checked at meter with everything on and getting a reading of 18.2 mbar.
 
Call transco your gov is goosed. Oh and you might have a piping issue to stove as there is more than a mbar difference
 
Last edited:
Call transco your gov is goosed. Oh and you might have a piping issue to stove as there is more than a mbar difference

Thanks Atouchofgas i will give them a call when i am back there tomorrow and will see if i can find where the pipe is buried
 
A quick phone call to Transco, new meter was fitted and everything was sorted. Once again thank you.
 
Status
Not open for further replies.

Similar plumbing topics

9 times out of 10 it just needs servicing & no...
Replies
8
Views
3K
Your gas rate is your big one to check. Well...
Replies
9
Views
163
Do you find a solution, I have exactly the...
Replies
11
Views
2K
tinodj
T
Thank you.
Replies
2
Views
99
1mb between meter and appliance with all...
Replies
5
Views
4K
Back
Top