I'm stumped and I could do with some help.
Went to a property today which has 3 floors. The property starts on the first floor of a building of 2 flats.
There are 2 toilets on the 2nd floor of this property (which is the 3rd floor of the building) which I believe are both tee'd into the same waste pipe going into the stack at the rear of the building.
Both toilets are the same design. When flushing either of them the water empties the pan right to the bend where the water seal breaks the siphonic actions, allowing the pan to refill. This happens on both toilets.
The waste pipe (viewing from the tee the smelly toilet is connected to) is full of standing water.
There appears to be no blockage as the water drains on both toilets. There is no leak behind the toilet (I had to remove tiled boxing in order to investigate).
The room where the smell is comes from the toilet nearest the stack.
I'm thinking that:
a) flushing this toilet induces a siphonic action and drains both toilet traps, momentarily allowing the sewer air into the property.
b) there is a partial blockage somewhere (the previous tenant used to flush her babies nappies down the lav :/)
c) The fall in the pipework is towards the toilets instead of towards the stack, hence why it's filled with water.
I've recommended rodding the stack before looking at pipework design.
Am I looking too deeply into this? Is there something I'm missing?
Any help would be grand as 4 other firms have been out and have basically run away from the job saying there is nothing that they can do, or denying that there is a smell (it's a bloody awful smell!).
Cheers all
Jay
Went to a property today which has 3 floors. The property starts on the first floor of a building of 2 flats.
There are 2 toilets on the 2nd floor of this property (which is the 3rd floor of the building) which I believe are both tee'd into the same waste pipe going into the stack at the rear of the building.
Both toilets are the same design. When flushing either of them the water empties the pan right to the bend where the water seal breaks the siphonic actions, allowing the pan to refill. This happens on both toilets.
The waste pipe (viewing from the tee the smelly toilet is connected to) is full of standing water.
There appears to be no blockage as the water drains on both toilets. There is no leak behind the toilet (I had to remove tiled boxing in order to investigate).
The room where the smell is comes from the toilet nearest the stack.
I'm thinking that:
a) flushing this toilet induces a siphonic action and drains both toilet traps, momentarily allowing the sewer air into the property.
b) there is a partial blockage somewhere (the previous tenant used to flush her babies nappies down the lav :/)
c) The fall in the pipework is towards the toilets instead of towards the stack, hence why it's filled with water.
I've recommended rodding the stack before looking at pipework design.
Am I looking too deeply into this? Is there something I'm missing?
Any help would be grand as 4 other firms have been out and have basically run away from the job saying there is nothing that they can do, or denying that there is a smell (it's a bloody awful smell!).
Cheers all
Jay