Installing a new bathroom and moved the loo not all that far from original location. Basically just turned it round… the fall I calculate to be too steep.. help!
Loo states 185 soil centre plus 4 mm for tiles and 6mm for backer on the floor we are going to be up at195/200mm off the floor. I make the centr of my existing beach to be 140 off the floor at best. A 50mm difference and a short run of only 80cm max…. Any advice welcome
 
Oh sorry just re-read it, you have 80 cm ( 800mm) you’ll be fine just connect it all up.
I thought you had 80mm, that would have been more challenging
 