macka09

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,248
Hi lads. I haven’t done one of these for quite some time but I’ve been asked to fit the towel rad with an element but the supplied valves are straights. It’s 500mm wide but whoever done the first fix have set the pipes at 400. Do I need to use one straight valve and one angled valve out of the tee for the element??
 
Also I am correct in thinking it’s filled fully as it’s also part of the heating circuit? Rather than if it was electric only
 
Also I am correct in thinking it’s filled fully as it’s also part of the heating circuit? Rather than if it was electric only

I have seen a ~ 300W electric towel rad that may have been oil filled, with thermostatic control but certainly had no connection to the heating circuit.
 
Also I am correct in thinking it’s filled fully as it’s also part of the heating circuit? Rather than if it was electric only
Yeah you fully bleed it and then in the summer months when the element is been used, the lockshied attached to the element is closed to prevent heat loss and the other valve remains open to allow for expansion. Just remember you can't use both the element and heating at the same time. It's one or the other.
 
I would not close the lock shield in summer. If the room comes up to temp of trv this will close and then there is no room for expansion should the towel rail get left on, more importantly heat dissipation- this will lead to a blown element.
Just leave lock shield as it is and don’t worry about the tiny heat loss through there.
 
I would not close the lock shield in summer. If the room comes up to temp of trv this will close and then there is no room for expansion should the towel rail get left on, more importantly heat dissipation- this will lead to a blown element.
Just leave lock shield as it is and don’t worry about the tiny heat loss through there.
How do we know a trv will be fitted? If there is then the trv will want putting on the element side so this can be turned off without effecting the lockshield. With all the elements I've installed, the manufacturers instructions have stated that when in use, one valve is to be closed and one is to remain open. I can imagine this is because you can't run both at the same time, if both valves are left open, and it's get a little cold and the customer puts the heating on, and forgets about the element, that will also cause damage to the element. You can remove your disagree rating too :p
 

Similar plumbing topics

  • Question
Hi everyone, I have an Eastbrook Hurley towel...
Replies
0
Views
1K
  • Question
About a year ago, I had the bathroom towel...
Replies
0
Views
3K
With CH selected on, if you open a hot tap...
Replies
2
Views
595
Yes the ufh should be separate from the rest...
Replies
1
Views
1K
Back
Top