Ok an update..
The reason this is being done is to prove there isn't a leak really, as I suspect the boiler.
For two months the combi boiler has been showing a drop each day of between half and one bar. And hence water is being added to the system.
It isn't coming out the prv, baloon over that, it isn't coming out condensate pipe.
No visible signs of leak.
Plumber pressure tested section where pipe is under screed, held 3 bar for 24 hours.
Pressure tested rest of system and saw drop...but after he left I found a tiny leak on rad joint, perhaps this was it.
Pressure kept dropping when boiler running.
Didn't want the house torn apart, as my suspicion is the boiler. It's only 3 months old.
Leak guy came round with thermal camera. All quite normal and we could see all pipe work with it.
Emptied system and pumped tracer gas in. No trace of leak. We opened every radiator bleed after checking to see gas was there and detector working which it was. Checked all pipe runs.
Finally pumped whole system to 2 bar with traver gas and left it to see if there was a drop.
After 2 hours no drop. Of course its freezing outside so had to get the system up and running again.
As far as logic goes, we have no leak. No point in tearing the place apart. ..the pipes run over head under plasterboard ceilings, we'd see a patch after two months of adding water.
The installer however didn't think it's the boiler.
I am now convinced there is a highly unusual fault with boiler, where we lose heating water in the exhaust when it is firing only.
Bear in mind I am a layman so this has been a nightmare. We are losing water but it is going nowhere. Unless I top up, boiler goes off.
I paid for the tests myself (600 quid so far) as no visible damage so no insurance.
I am now going to insist the boiler is faulty and get the manufacturers to replace parts. Someone here suggested secondary heat exchanger could be to fault.