Called out to a customer with a Trianco TRO 12-14 boiler, has been cutting out.
Burner is the old "upside down" Bentone electro oil type
Did the usual service and tried to fire it up. Smoke high. Opened air plate to get smoke down. CO2 to about 6%, but Carbon Monoxide at over 1,000ppm. Methinks blocked flue. Customer hasn't had the flue swept for years. Flue swept with loads of soot coming out. Baffles in good order.
Come back to try again, hardly any difference. Crazy CO reading again (air inlet fully open). 0.50 80 EH nozzle and the pump pressure is set at 100psi as per instructions. Noticed that the flame is oscillating, causing the ignition to fire periodically.
Trianco suggested that oil may be leaking from the back of the nozzle. Wrapped PTFE round the nozzle and defnitely no oil leak. Stumped now. My feeling is that it could be the pump (re the oscillating flame). Before I rush out and get a new pump, what does anyone else think?
Burner is the old "upside down" Bentone electro oil type
Did the usual service and tried to fire it up. Smoke high. Opened air plate to get smoke down. CO2 to about 6%, but Carbon Monoxide at over 1,000ppm. Methinks blocked flue. Customer hasn't had the flue swept for years. Flue swept with loads of soot coming out. Baffles in good order.
Come back to try again, hardly any difference. Crazy CO reading again (air inlet fully open). 0.50 80 EH nozzle and the pump pressure is set at 100psi as per instructions. Noticed that the flame is oscillating, causing the ignition to fire periodically.
Trianco suggested that oil may be leaking from the back of the nozzle. Wrapped PTFE round the nozzle and defnitely no oil leak. Stumped now. My feeling is that it could be the pump (re the oscillating flame). Before I rush out and get a new pump, what does anyone else think?