Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Turbomax VUW 242 boiler problem with hot water in the Boilers area at Plumbers Forums

Messages
9
Hi all
So we still have this very old boiler but we have still having problems with the hot water, we have called out 3 repair engineer's, but as it's a old boiler everyone seems to guessing, so far they have changed the thermistor, secondary heat exchanger, primary heat exchanger, diverter valve also done a power flush, new radiators as well but for some reason the boiler seems to be turning off and on every few mins, and the hot water is from burning hot to warm.
Can someone guide us to what the issue could be so I can tell the repair engineer's exactly what to look at. I don't mind any experienced engineer on here who is local (west london) to me to come take a look, we have spent so much on this boiler we can't afford to get a new one at the moment. Thanks in advance
 
Have they cleaned the internal filter ?
 
No there’s a filter inside the boiler
 
Could the modulating value need replacing ? It's so hard to understand, the engineers have replaced all the usual culprits but it still seems to be the same
 
No there’s one on the heating side
 
Correct
 
I'm assuming problem on DHW side only?, can you open a (one) HW tap and measure the flowrate.
If you open all HW users does the boiler continue to fire?.
Do you have DHW temperature control as well as CH water temperature control?.

Your boiler has a max output of 24kw so if you can ensure a total flowrate of just > 6.5/7LPM then even if the boiler is not modulating the DHW temp should remain < 65C and not cause a boiler trip. If it is modulating to its minimum output of 9.6kW then a flowrate of only 2.7LPM will achieve the above.
 
Last edited:
I'm assuming problem on DHW side only?, can you open a (one) HW tap and measure the flowrate.
If you open all HW users does the boiler continue to fire?.
Do you have DHW temperature control as well as CH water temperature control?.

Your boiler has a max output of 24kw so if you can ensure a total flowrate of just > 6.5/7LPM then even if the boiler is not modulating the DHW temp should remain < 65C and not cause a boiler trip. If it is modulating to its minimum output of 9.6kW then a flowrate of only 2.7LPM will achieve the above.
Hi the problem is the DHW side only but I've noticed it modulates when the CH is on as well, the temp hits 65c and goes off, can't understand much
 

Similar plumbing topics

Which Vaillant boiler is it?
Replies
1
Views
357
B
No the installers need to come out
Replies
10
Views
2K
R
Wb 4000 recently installed, and just balanced...
Replies
0
Views
528
Return temperature
R
M
Hello, We’ve recently moved into a fairly old...
Replies
0
Views
587
MartinPod81
M
You've already spent thousands on a new boiler...
Replies
2
Views
954
Back
Top