U/F heating directly off a combi | Plumbing Jobs | The Job-board | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss U/F heating directly off a combi in the Plumbing Jobs | The Job-board area at Plumbers Forums

chris watkins

Esteemed
Plumber
Messages
5,067
Has anyone taken an under floor heating system straight off a combi or heat only gas boiler without using a blending valve or mixing header ?
If so, did it work & was there any problems with the boiler controlling the water temperature?

The boiler operating temp range can be fixed (heating side only) to 50 - 30deg C on the board.
I know the limitations on the boiler pump but it is a very small circuit & there in maybe another problem as the heating load at -3degC is only around 3.5kW, the boiler has an anti-cycling timer which hold it off for 3mins but just not sure if this will work correctly.
Help Please, thanks Chris.
 
Is that the only circuit eg no rads ?
 
its going to cycle like a mother i would close tee it

if you can set it up right eg the temps cant see why not just label the temp knob as do not touch due to under floor etc
 
diy?
 
I remember doing a job in London must be at least 25 years ago which was all underfloor, it had 2 large blending manifolds one on each floor, fed by a heat only Ideal iMax condensing boiler on which you could set the operating temperature to give a maximum of 50deg C flow.
I couldn't understand why the boiler was then set up to give high temp water which then had to be blended down to give no more than 50 at the manifolds, it didn't make sense as boiler could have been in condensing mode all the time.
 
I remember doing a job in London must be at least 25 years ago which was all underfloor, it had 2 large blending manifolds one on each floor, fed by a heat only Ideal iMax condensing boiler on which you could set the operating temperature to give a maximum of 50deg C flow.
I couldn't understand why the boiler was then set up to give high temp water which then had to be blended down to give no more than 50 at the manifolds, it didn't make sense as boiler could have been in condensing mode all the time.

Separate hot water boiler ?
 
Yes, electric cylinder for some reason, it was a large doctors surgery so not much required.

Sometimes it's due to them wanting a back up eg heating goes off they can still work etc
 
24kw vaillant combi.
Rated it down to min kw. And big marker pen on thermostat setting. Bit crude, but does the job.
I think you can adjust max temp on a ecotec.
Boilers are all in locked cupboards, so no one messes with them.
 

Similar plumbing topics

E
I reckon if I did a survey of 100 heating...
Replies
0
Views
461
eco-heating options
E
M
Hello, We’ve recently moved into a fairly old...
Replies
0
Views
631
MartinPod81
M
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
909
HRP123
H
  • Question
I had a chattering float valve in the loft...
Replies
2
Views
458
Back
Top