Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss UFH floor temp control in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
P

Pickled eggs

Hello,

We are having wet UFH installed across the ground floor of our house, about 5 zones. We'd like vinyl and timber and hence know we need to limit the floor temp to 27 degrees; question what are the ways to do this?

We've seen the neo control system that can control on air temp and floor probe temp.

We're keener on the hive system, but we'd need a secondary control for the 27 degree cut off. This must be the same as having standard room stats - how is floor temp controlled in that situation?

Many thanks
Joanne
 
I was going to say exactly the same thing as Shaun, Wojtek is the man :)
 
Just fit floor temperature probes into all floors with vinyl. Then set the stat limit to 27.
Forget the hive, they are useless at controlling underfloor heating. There is too much lead and lag with underfloor for a predictive thermostat..
 
  • Like
Reactions: rpm
neo stats all day long you can get a hub to control neo stats from your phone why would you need hive?
 
Just run the flow temperature at 45C.
Without going into calculations and reasoning of calculations, a flow temperature of 45C will give you an average floor temperature of 27C - 28C - give or take.
 
Personally I wouldn't recommend hive thermostats. waste of time and money. not just heatmiser, but quite a few decent quality thermostats allow user to set probe limit whilst using air sensor to control the room temperature.
 
Status
Not open for further replies.

Similar plumbing topics

As part of deep house renovation, planning to...
Replies
0
Views
876
Anyway, you can always increase the boiler...
Replies
16
Views
1K
That is true - however with Vaillant...
Replies
4
Views
848
Yes, a very interesting proposal, I asked that...
Replies
1
Views
1K
Back
Top