waxworks59

Hi - I hope you all are well

We have recently moved into a new house that has under floor heating. The house had an extension built to it, the under floor is heated by gas. The original house had underfloor heating as well, powered by electricity.

The under-floor heating in the extension does not work. I tried to attach a picture of the system we have (I hope it worked)

The control on the wall does not seem to interact with the system
(ie, when i put the heat up, it does not react). When looking at the installation, I see a white box that has a 'manual' and 'automatic' switch. It currently points to 'automatic' however when I switch it to 'manual' the boiler comes on and I feel hot liquid going through the copper and pvc pipes. However the floor itself does not heat.

The pump installed is a grundfos 25-60 and am inclined to say the pump does not work (as the floor does not heat up..)

How can I check if the pump is working ? (is there a reset button?)
How can I check if the control is communicating with the system ?

The installation has quite some valves (Red/Blue) all are open. I have not touched these. What would Red/Blue mean ?

There are in total 4 PVC pipes, two of them get heat when I switch to 'manual', two don't.

Any help on the questions and how I maybe could fix this myself ?

In terms of operating the under floor heating (for both gas and electricity), what is the advise, ie letting them on day&night on a (which?) temperature or switch them only whenever needed to reduce costs ?

Thanks a lot !!
 
With UFH you have to wait for the slab to heat up.
It is not an instant form of heat like radiators.
Two of the pipes heat up - that's a good sign, wait a few hours and see if the other pipes get warm.

As for your thermostat - does it have batteries? Replace them.

As for operating temperatures - you should set a minimum level on the thermostat at @ 18 C.
You don't want the slab to get cold because it will take too long to heat up again.
 
Hi Oz-plumber - thanks a lot for your insights

the thermostat is on batteries indeed (plugs into a wall as well), will replace them and see what happens, and you are spot on, each time i tried it for about one hour and nothing really happened, i ll leave it on for a longer time and see what the result is. Thanks again
 

Similar plumbing topics

  • Question
I used wd40’s silicone spray version
Replies
6
Views
919
  • Question
Yours is an old fotic cylinder, Thermal store...
Replies
1
Views
1K
System boilers have a pressurised heating...
Replies
1
Views
360
  • Question
The user, installation and wiring...
Replies
11
Views
1K
  • Question
Hello, I am just catching up on some threads...
Replies
1
Views
634
Back
Top