Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Underfloor heating 1 room not warming up in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
U

Unregistered

Hi,
I'm hoping somebody could offer some advice. we have an underfloor heating system in 2 rooms (seperate zones, thermostat in each) it works fine in the first room but in the second room it doesn't get warm. what is confusing is the return feed for this room is hot so water is running through it but the room remains cold not even warm. has anyone ever come across anything like this?

It's got me stumped...

Thanks in Advance!
 
So if you're saying that the actual loops are all getting hot....but the room is still cold - then it must be a bad design. Or maybe the flow rates are wrong and the system isn't balanced. How long has it been in?
 
is the return warm ish?
 
OP please register with us. You will get more answers
 
Hi Thanks for the replies,
I am can confirm the return is definitely hot not just warm I can't give accurate temperature readings but to generalise , zone one heat output is 100% heat return is about 60% zone 2 output is 100% return is about 95%. zone 1 warms up but zone 2 remains cold. this system has been in place for about 18 months and last winter worked fine, it was shut off during summer and I turned back on last week. I'm an engineer (electrical) so have a bit of common sense (a little bit!) but I can't figure out what could have happened since last year that could have caused this. its almost like during the summer someone broke in ripped up my floors and stuck a load of lagging on the pipes! (pretty sure they didn't before anyone suggests that!)



Thanks for the tip Riley I'll register now.
 
can you feel any flow though the return/ flow indicator?
 
Please register with us and start a new thread to receive additional answers to your question.
 
Status
Not open for further replies.

Similar plumbing topics

I started a long winded response but deleted...
Replies
1
Views
731
sticking actuator, try changing it over whith...
Replies
3
Views
764
  • Question
Might be worth testing with two zones off try...
Replies
1
Views
1K