I have a client with an open plan kitchen/dinner/lounge complaining it is freezing cold, basically a big room with double glazed patio doors leading onto the garden and 12 sky lights in the roof, the dimensions are 7.2 long x 4.5 wide x 2.45 high and all they have is a 4ft column radiator!
Because of the U value nightmare I have manually calculated Fabric & Ventilation losses, F1 & F2 factors and have came to a sum of 6350 watts of heat needed, I'm confident my calculations are correct.
The problem I have is I cant find a radiator rated to the number of watts needed above, so now I'm thinking two radiators but I only have the existing flow and returns to use as the floor is tiled, will the flow/return cope with this?
Any ideas or suggestions welcome
Thanks
Sam