Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Unvented cylinder with no system boiler? in the Boilers area at Plumbers Forums

Messages
9
our client does not want a gas fired system boiler but he wants to keep his hot water storage. Its currently open vented via an old back boiler. The back boiler has been removed and electric rads installed

So can we install an unvented system without a gas boiler? The cylinder to have x2 3 kw immersions.
Is this ok!?

Is there a better alternative?

Dynamic and standing pressures good
Flow rate 21 plus
 
Another point is that you need to get an electrician to confirm that that the electricity supply cable can handle the proposed extra load. If the supply and/or house wiring is not already up to the job, upgrading can be very pricey.

Agreed.

Each heater element is going to take about 13A, so the house wiring is probably OK for THIS load, BUT there are electric rads, so a total load calculation would need to be undertaken, to make sure, as you say it is OK for this EXTRA load (caps aimed at the OP).

I would suggest each element should have a dedicated feed from the DB. These would need to be 20A, probably using 2.5mm cable. You could but a 32A feed in, probably 4mm cable, maybe 6mm, and split locally, but there would need to be some local protection if you don't want to be connecting 32A protected cables, ie the 4mm or 6mm, into the immersion heaters. I also suspect the manufacturer would specify protection lower than 32A.

To be fair that would probably be cheaper than a boiler. My concern would be recovery time and running cost.
 

Similar plumbing topics

Look at a Viessman 222 10 year manufacturers...
Replies
10
Views
2K
This one is taking shape now bit of a change...
Replies
7
Views
111
Replies
5
Views
1K
I use a bit of foam to hold it in place, then...
Replies
41
Views
5K
200mm apart ffs not good if not a very good...
Replies
18
Views
2K
Back
Top