Hello all

I'm installing an unvented vaillant unistor cylinder. The parts in the box includes a single two port valve.

Thing is there is no 3rd party wiring diagram in the installation manual showing how to wire this two port valve into a y plan system.

Has anyone got that diagram? I have contacted Vaillant but they are slow in response.

I'm BPec unvented qualified.

Cheers
 
On a y plan system wire the two port to the safety thermostats

Eg when upto temp eg 60 the port valve closes

TBH convert the system to an s plan
 
Megaflo Wire Y plan.png



Vaillant Y plan cons.png

Just incase you still needed the wiring, the Vaillant stats connections replace the Megaflo ones as follows
1 = 1 on high limit (upper part).
2 = 2 on control stat (lower part)
3 = 4 on control stat (lower part) the terminal marked with the 1 in a circle.
 
two ways

if you cant get back to the multi way/system wiring centre

take your power from the immersion and make safe the rest of the wires

or the better way

take your power from the hot water on link it through the stat and then to the valve
 
two ways

if you cant get back to the multi way/system wiring centre

take your power from the immersion and make safe the rest of the wires

or the better way

take your power from the hot water on link it through the stat and then to the valve
I think I will stick to the MI's, immersion sound like having a double feed into the controls wiring to me & not so sure of any benefits the other way as you still have to run it through the stats.
 
I think I will stick to the MI's, immersion sound like having a double feed into the controls wiring to me & not so sure of any benefits the other way as you still have to run it through the stats.

They wouldn't be connected as you couldn't get wires from the heating eg not accessible

So the port valve would act on its own via it's own fused spur from the immersion etc
 
Hello
Thanks very much to all those who gave input. Here's what I managed to get from Vaillant which looks good to me.

Only question is, how does the 3 port get a signal to move to hw mode?

Why this diagram is not in the manual is beyond me.
 

Attachments

  • ecoTEC 2012 Y Plan Wiring Diagram.pdf
    201.5 KB · Views: 36
Via the orange wire off the two port
 

Similar plumbing topics

  • Question
Hello all I'm replacing 2 unvented cylinder a...
Replies
0
Views
841
C
  • Question
Thanks for replying matey. You've been a...
Replies
3
Views
1K
  • Question
Ya, they said the fact the anti-vibration...
Replies
6
Views
712
Who said plastic 28/22mm copper tube and mlcp...
Replies
3
Views
833
  • Question
Morning, he took it out from where it was...
Replies
11
Views
957
Back
Top