Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Unvented heating system, unusual boiler fault in the Boilers area at Plumbers Forums

Pauld1962

DiddlyP
Messages
9
Called to a customer today and the system boiler keeps repressurising on its own ... After I dropped out all the pressure I watched as it refilled ... The filling loop was disconnected at the time ... Customer reports that it's never done it before ... The only way I could stop it was to turn off the cold mains ... !! ... Any help appreciated ..
 
Combi boiler ?
 
It's an old system boiler Vaillant thermocompact vu 282/1e ... Unvented cylinder ... Is there a test for split coil and what causes it ... They use the immersion most of the time as solar power is available ..
 
Drain & valve off cylinder coil in that way they can still use the immersion or Solar for domestic hot water.
The heating system pressure should stop rising. If so it is the coil & you will have to order a new cylinder.
 
I isolated the F&R at the boiler at 1.5bar and it held .. Once the return was opened the pressure rose immediately and water meter was turning over .

Probably cylinder coil gone then.
Is it a copper unvented cylinder, or stainless steel?
If you are not G3 qualified, just be aware if no isolating valve on mains supply to unvented cylinder, then only install one BEFORE the combination valve. (Between the combination valve and cylinder must not have any valve)
 

Similar plumbing topics

I'm going to go tomorrow to switch it off for...
Replies
10
Views
690
P
Tricky situation for you. Boiler shouldn't...
Replies
2
Views
437
M
Isolate and drain boiler. Pump up expansion...
Replies
1
Views
729
  • Question
I would suggest getting a G3 plumber in to...
Replies
9
Views
425
Back
Top