Hi there,
Third call back today. Bit of help please. Installed Telford easy fit unvented cylinder 3 weeks ago. Over heat stat has started tripping on cylinder leading to no hot water. Primary circuit for the coil set at 73*C so no where near manufacturers cut out temp of 83*C.
When I'm there and have the hot water on if I turn the cylinder stat down it closes the 2 port valve and turns the boiler off so it's wired in correctly and that side of it is ok.
Presuming it's a faulty stat but just wondering if there's anything I might be missing???
Cheers