Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Uponor underfloor heating valve. in the UK Plumbers Forums area at Plumbers Forums

Christopher buzzard

Gas Engineer
Messages
190
Can some please identify the valve on this underfloor manifold ( with the black wire coming out of the top). Have an issue where the system is turning off every 10-20 minutes and staying off for a while then coming back on again. The room can’t get up to temperature because of this. Power was going to the valve but not out of it.
‘thanks for your help.
 

Attachments

  • 60D0F2CE-8DB2-4E0F-8C99-869D1D955135.jpeg
    60D0F2CE-8DB2-4E0F-8C99-869D1D955135.jpeg
    116.7 KB · Views: 37
It looks like an temperature sensor on the heating outlet of the pump.
If the temperature gets too hot the pump will stop operating - to protect the UFH pipe and the floor.

Adjust the mixing valve to get cooler water or it could be a faulty thermostat sensor
 
Christopher,

That is a TM manifold, the originally fitted high limit stat will be hard to source. The current Uponor part number is 1002371 - which may need a threaded insert to fit.

Don’t be tempted to just bypass the limit switch
 
So only there if the thermostat head on the flow, fails and or if the boiler thermostat fails?
Never seen them on a manifold before. Spoke with an electrician who said in the past he hasn’t wired them in. (Not saying he’s right to do that though)

Yes in the event of flow temperature being too high due to whatever reason this will isolate supply to protect floors and pipework as said above.
 
Brambles is the man on these so he is worth listening to lol. As he said linking out is not advisable, in many cases will give a quick fix or in this case find a fault but it shouldn't be left like that.
 

Similar plumbing topics

  • Question
Can anyone help with this underfloor heating...
Replies
1
Views
398
  • Question
Hi, I have I blend valve from Nu-Heat ( they...
Replies
0
Views
667
  • Question
Or if 3.7LPM/zone = 14.8LPM
Replies
19
Views
2K
  • Question
I used Uheat 5 years ago. Wanted to try out...
Replies
13
Views
2K
  • Question
I think it maybe best to contact Drayton for...
Replies
7
Views
3K
Back
Top