Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Upstairs Toilet Draining into ground floor soil stack. in the Boilers area at Plumbers Forums

Messages
2
I'm looking to connect an upstairs toilet into an existing ground floor soil stack. Is the solution I've drawn out possible or does the soil stack vent need to be above the connecting appliance still?

Red is the proposed new pipework and brown the existing.

Let me know any questions.

Toilet Drain.png
 
https://assets.publishing.service.g...achment_data/file/442889/BR_PDF_AD_H_2015.pdf
I have a question, do you don't that what you are proposing is covered by the Building Regulations & is notifiable to your local BCO?
What is required is set out in the attached link to AD Part H (1).

If you are not sure what is required employ someone because your drawing means nothing unless we can see it in context of the building & the appliances connected.
 
Last edited:
AAV will need to be above all of the appliances going in to it. 200mm above the flood level (rim) of the basin in your new bathroom, otherwise when water backs up in a blockage it pours out of the AAV rather than backing up into the basin where you can see it and deal with it. Check regs as above
 

Similar plumbing topics

Thanks, I think its a case of stick with the...
Replies
4
Views
843
No problem with the 900mm from openings as it...
Replies
4
Views
322
10 o’clock / 45 degrees would be better than...
Replies
3
Views
577
Sorry for the late post on this but just...
Replies
23
Views
2K
F
Thanks for your reply. I don't think so. I...
Replies
3
Views
1K
Funkymunkey27
F
Back
Top