danielp

Hello, Having trouble with the above status on hot water if the tap is open on full the water goes cold but perfectly fine half way open?

replaced the plate heat ex

also the customer said it had came up with an f23 fault in the book says pump or ntc even those the pump is working well on the radiators is there a chance it may not be for hot water just seems when the burner ramps up it brings out this status and the heat not circulating through the plate quick enough thanks
 
Take off the rubber hose from pump to main heat ex and rubber hose from heat ex to the flow manifold....and clean out...these always get stuffed full of magnatite and also remove low pressure sensor give it a clean....i had this fault not so long ago and i just removed all the pipework inside the boiler and cleaned it out and it was fine.

Sent from my GT-I9100 using Tapatalk 2
 