vaillant ecotec 418 erp (open vent) | Plumbing Jobs | The Job-board | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss vaillant ecotec 418 erp (open vent) in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

BLOD

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,308
how the hell do you get it to run on max & min ? - (instructions are a load of rubbish) Spent nearly 40 mins waiting for their tech line to answer then gave up.
 
Po1.
If it's the new energy erp.from memory Turn off power then turn on while holding mode for 10 sec. Po should come up scroll to Po1 and change to 100 for max 0 for min press mode
 
It's really frustrating, boiler itself seems good but the installation manual is just a joke, and tech help line is impossible.
Come to think of it I've never had to call a manufacturer before when doing an install
 
Po1.
If it's the new energy erp.from memory Turn off power then turn on while holding mode for 10 sec. Po should come up scroll to Po1 and change to 100 for max 0 for min press mode

Thanks for this buckley, yes it's the erp one, why doesn't its tell you this in the instalation instructions ?
 
Ahh good old vaillant... Impossible instructions, no help after installation, no part numbers in book, no reply from there email departments... Yet people sing there praises... I'll stick to Bosch thanks :)
 
Thanks for this buckley, yes it's the erp one, why doesn't its tell you this in the instalation instructions ?

I am talking the latest version. Which is the gliwworm aluminium heat exchanger
 
Buckley, do you mean the coil or square type heat ex ?
 
If it's like the new glowworm then think it'd this mate this is the glowworm details which should be the same
 

Attachments

  • DSC_0930.jpg
    DSC_0930.jpg
    94.7 KB · Views: 8
  • DSC_0931.jpg
    DSC_0931.jpg
    92.5 KB · Views: 7
Last edited by a moderator:
Just had similar issue with new EcoTec 832 comes set on auto, installer has to reconfigure boiler for heat load of system, what happened to the days when boiler just fired up and got things hot, now need a degree in physics just to turn it on. But did find instructions left out some details on setting up boiler
 
Status
Not open for further replies.

Similar plumbing topics

Hi There, What did you decide to do in the end?
Replies
1
Views
546
Absolute cock & bull from SGN, think about...
Replies
8
Views
2K
Hi, thanks for the reply, that did cross my...
Replies
2
Views
877
Yep I think that’s got to be the next step. I...
Replies
8
Views
2K
    • Like
Great summary and well done for getting it...
Replies
1
Views
2K
Back
Top