Hello,
We got a Vaillant Ecotec Exclusive Green IQ 835 combi boiler in November 2021 as we wanted the most efficient boiler that modulated really well, especially for heating.
Two weeks after the installation, the heating engineer needed to recalibrate the boiler and after that we started having problems with modulation for hot water. Vaillant states that the modulation will kick in for a minimum flow of 1.8l, but even if we were running 3.5-4l, the boiler would just shoot up to maximum, overheat the water and turn off the burner, then start it up again and turn off, like before. This would usually happen if someone opens the tap on a lower flow from the beginning, so it looked like the boiler could not read the flow properly.
When we look at the live monitor, it looks like it starts cycling at the "measuring program", it never gets to the stage "Burner on".
Vaillant sent about 4 engineers our way who replaced multiple parts, from the CO2 sensor to the whole motherboard in the latest instance, and it was still doing that. We have been opening tap on maximum, waiting until it starts modulating and then turning the flow down to use it.
Vaillant agreed that the boiler should not be doing that, especially at 4litres. There was nothing else they could do, so they replaced the boiler.
The new boiler worked absolutely fine for over a month. Unfortunately it has now started doing the same thing. There have been no changes in use or any intervention. Has anybody seen anything like this before, could anyone suggest where to look, or what else we can try?
Many thanks
Julia
We got a Vaillant Ecotec Exclusive Green IQ 835 combi boiler in November 2021 as we wanted the most efficient boiler that modulated really well, especially for heating.
Two weeks after the installation, the heating engineer needed to recalibrate the boiler and after that we started having problems with modulation for hot water. Vaillant states that the modulation will kick in for a minimum flow of 1.8l, but even if we were running 3.5-4l, the boiler would just shoot up to maximum, overheat the water and turn off the burner, then start it up again and turn off, like before. This would usually happen if someone opens the tap on a lower flow from the beginning, so it looked like the boiler could not read the flow properly.
When we look at the live monitor, it looks like it starts cycling at the "measuring program", it never gets to the stage "Burner on".
Vaillant sent about 4 engineers our way who replaced multiple parts, from the CO2 sensor to the whole motherboard in the latest instance, and it was still doing that. We have been opening tap on maximum, waiting until it starts modulating and then turning the flow down to use it.
Vaillant agreed that the boiler should not be doing that, especially at 4litres. There was nothing else they could do, so they replaced the boiler.
The new boiler worked absolutely fine for over a month. Unfortunately it has now started doing the same thing. There have been no changes in use or any intervention. Has anybody seen anything like this before, could anyone suggest where to look, or what else we can try?
Many thanks
Julia