Hello
Our Vaillant boiler has developed a fault in the last 2 weeks. The hot water is working without any problems. However, within 15-20 minutes of turning the heating on we are getting the error message 'F.75 Fault. Pump water shortage'. The boiler being on for heating is pushing the filling pressure above the max 3 bar it seems, which I assume is causing the shut down. To get it working again I push the reset button.
Do I just need to let some water out of a radiator?
For obvious reasons, I'd like to try to avoid calling someone in at the minute...
Thanks
JJ
Our Vaillant boiler has developed a fault in the last 2 weeks. The hot water is working without any problems. However, within 15-20 minutes of turning the heating on we are getting the error message 'F.75 Fault. Pump water shortage'. The boiler being on for heating is pushing the filling pressure above the max 3 bar it seems, which I assume is causing the shut down. To get it working again I push the reset button.