Hello all,
I’m looking for some advice on my Vaillant boiler, which is controlled by my Hive thermostat. I have set the radiator flow temperature to 75 degrees on the boiler control panel, but the actual temperature never gets hotter than 50. I have done some checks, and believe I have found the problem:
I don’t actually understand what an eBUS is, so I’d be really grateful (and a lot warmer!) if someone could let me know the following:
Many thanks,
Joe
I’m looking for some advice on my Vaillant boiler, which is controlled by my Hive thermostat. I have set the radiator flow temperature to 75 degrees on the boiler control panel, but the actual temperature never gets hotter than 50. I have done some checks, and believe I have found the problem:
- If I put the boiler in test mode, it very quickly heats up to 75 degrees. As soon as I leave test mode, it drops back down again to 50.
- On setting D.005 in the installer menu, the value is showing at 50 degrees. I think this is what’s causing the issue.
- The manual suggests that this setting can be changed by adjusting D.071, and an ‘eBUS control’ can override this setting if fitted.
- D.071 is set to 75 degrees.
I don’t actually understand what an eBUS is, so I’d be really grateful (and a lot warmer!) if someone could let me know the following:
- Is it possible to disable or adjust the eBUS settings from the boiler control panel?
- If not, how would I go about fixing this problem, and is it a job that requires a professional?
Many thanks,
Joe