Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Vaillant Sustain 28kw Combi Heat Input in the Gas Engineers Forum area at Plumbers Forums

richard978

Gas Engineer
Messages
171
Could anyone tell me whether the Vaillant Sustain heat input is noted in gross or net please.

I was sure it was NET but someone has said it's gross which makes no sense at all. I work all my gas rates to NET so if I'm wrong my gas rates will be way out.

I've included the data badge.
 

Attachments

  • PXL_20240624_122555638.MP.jpg
    PXL_20240624_122555638.MP.jpg
    668.5 KB · Views: 33
Will be Net as it would be a 25kw combi
 
That's what I thought because it would not be a 28kw boiler now days with a gross figure. I was worried I'd got my figures all wrong.....
If you mean the fuel input then that is the gross heating value, that's what you are paying for.
Yours, I think is a "28kw" and is limited to give 18.5kw to 20.1kw output to CH but gives 28kw output to HW (combi mode), it gives a DHW flowrate of 11.6LPm @ a dT of 35C which equals a output of 28.33kw, the fuel input, depending on whether partially condensing or not, probably not in DHW combi mode, might be ~ 32/33kw or approx 2.9/3.0m3/hr of N.gas. The sustain apparently gives the same CH output in the 24kw, the 28kw & the 34kw models but gives DHW outputs of 24.4kw, 28.5kw & 34.6kw.
 

Attachments

  • Vaillant ecotec-sustain-combi-installation-and-maintenance-instructions-2055538.pdf
    9.3 MB · Views: 26

Similar plumbing topics

The percentage should be in your book. It is...
Replies
2
Views
3K
E
It sounds like that needs to be sealed from...
Replies
3
Views
1K
Replies
3
Views
716
No that’s how it’s supposed to work and is set...
Replies
12
Views
3K
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
Back
Top