Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss vaillant vcw sine 18 in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
1,582
does anyone know how to take gas inlet pressure on this beast of a boiler and gas valve.there is a test nipple on the gas inlet pipework buts it's behind the boiler and impossible to get at..or is it..and i'm after the manual.
 
Last edited:
Have a butcher's here

[DLMURL="http://www.gotogasdocs.co.uk/boiler-manuals/232-vaillant"]Vaillant Free Boiler Manuals Free Gas Manuals[/DLMURL]
 
Last edited by a moderator:
If you can't get to the nipple gas rate it.
 
from memory isnt there a test nipple just above the gas valve on the inlet to burner
left of dead center as you look at it or if its room sealed i think its on base of combustion chamber looking down again to the left of gasvalve you can do inlet working preasure from by the gas shut of valve on the jig
 
Just been to one of these today, I could manage to get to the inlet pressure, it is on the side of the gas valve right at the back, a pain to get to. Anyway i checked the burner pressure which should have been 10.6mb it was 12.5 and the combustion ratio was reading 0.0056. very high. Does anyone no how to adjust the burner pressure on these boilers???? I'm struggling
 
these old beasts were never made to be combustion tested ,is it this one with the little wire sealed door/flap on the front of the solenoid for adjustment im just getting the book but its a long download
 
pictures in the book ive found dont show it clear but im sure it was under a cap or flap that was wire sealed on right side above the solenoid its definately not the adjusting screw near the base of the solenoid thats a slow ignition device
 
Adjusting the inlet pressure isn't going to affect the readings.
It needs a strip down service.
 
I have stripped it down and cleaned, the burner pressure was up to 12.5mb should be 10mb according to mi. The ratio was about 0.0056. Some one said that after a service the ratios will be higher than normal for a while until it settles, how true is this. ??? I had to AR it anyway until I can work it out. Was hoping I could make some adjustments on it. Although its very old
 
Ok just to finish this thread off:

Went back to the boiler today. Check ratios. 0.0056 again. Well high. Burner pressure 14mb. Well high. Took boiler to pieces to out heat ex changer, straightened out all the fins, cleaned of all the calcium spots all over it, noticed a big split in the heat exchanger and a big hole on the back. Cleaned burner and put heat ex changer back. Adjusted burner pressure back to 10.6 mb as MI stated, (As someone said I think it was Ray, the burner pressure adjustment is under a sealed flap above the differential valve) and fired it up! Took my ratios again and it was 0.0008 - 0.0012.

Very happy with that! Anyway I ID it in the end because the case had a small split in it, I rang Gas safe technical and they said I was not being over cautious to ID it.

New boiler time. Thanks for the help...... Till next time
 
Status
Not open for further replies.

Similar plumbing topics

Thank you for the replies. I had another...
Replies
4
Views
836
Absolute cock & bull from SGN, think about...
Replies
8
Views
2K
R
Hi, I have boiler Vaillant VUW SOE 242_2-3 R2...
Replies
0
Views
576
Revlyne
R
More than fine then in 11/5 tube should be...
Replies
3
Views
629
Hi, thanks for the reply, that did cross my...
Replies
2
Views
820
Back
Top