Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss vaillant in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

hammers4spanner

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
7,703
fitted a vaillant system boiler 46 kw and flashed it up today was running fine then it flashed up s.85 and s.97 which alternated between the two .
Done all the usuals hot flush chem clean so has been fully drained/cleaned , book indicates demand for heating blocked little bit baffled as seems to be running o.k still .
any ideas anyone as job finishes monday so need to sort this asap
 
system is running fine but throws up a service required press the info button and those codes come up??
 
46kw must be commercial? You definitely getting the heat away O.K?
 
fitted a vaillant system boiler 46 kw and flashed it up today was running fine then it flashed up s.85 and s.97 which alternated between the two .
Done all the usuals hot flush chem clean so has been fully drained/cleaned , book indicates demand for heating blocked little bit baffled as seems to be running o.k still .
any ideas anyone as job finishes monday so need to sort this asap

Don't that size specify a low loss header
 
It's classed light commercial and heats up a treat no issues their

I did have a header and diet may installed but was told to remove it by mechanical engineer as was not on spec .I do have a strainer installed on return which have not around to checking as ran out of time
 
It's classed light commercial and heats up a treat no issues their

I did have a header and diet may installed but was told to remove it by mechanical engineer as was not on spec .I do have a strainer installed on return which have not around to checking as ran out of time

You need it back on as I'd say that's your proem MIs state it tell the ME to do one
 
Status
Not open for further replies.

Similar plumbing topics

2021 and I have still got my trusty turbomax...
Replies
10
Views
5K
Jiten bulsara
J
Check the magna valves.
Replies
9
Views
3K
Hello All- (Usual caveats apply: I am the...
Replies
0
Views
172
    • Like
From this post, I think you’ve got a good...
2
Replies
47
Views
6K
  • Locked
Thanks guys - some good advice! Think I'll go...
Replies
12
Views
14K
Back
Top