Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Valiant Ecotech Plus 637 - Error F76 in the Central Heating Forum area at Plumbers Forums

Messages
102
A couple of weeks ago my Valiant Ecotech Plus 637 displayed Error F76. Boiler is 13 years old; serviced annually.

I power cycled the boiler and it operated for ~10 days before hitting the same error again; I once again power cycled the boiler and it was in operation for ~24 hours before displaying the F76 once again. I power cycled it and it ran for just a few hours before hitting F76 for a third time.

I have now power cycled and done a P0 test and the boiler is back in operation for the last couple of hours.

Clearly this isn’t the thermal fuse and I would be suspect if it is wiring given the fact that reset clears this condition. I have come up with a potential trigger however… Whilst the central heating side of the boiler has been untouched; I have over the last couple of weeks turned the water off for a period and drained some hot water from the megaflow. Once was as we were away for several days (I did turn off the H/W heating whilst away). On our return we hit this error 4 days later. Yesterday, the water was turned off and some H/W drained to replace a shower.
 
its an overheat ntc on the boiler that will throw that fault, try turning temp. down to 50, running boiler for a day or two make sure your air bleed is open on pump, see how that goes.
 
So, I lowered the radiator temp to ~55 degrees and ever since the boiler has been stable. It must be temperature related but clearly my boiler must have an underlying fault. I will have a plumber check the wiring etc but it will get me by for now. I'll tend to it ahead of the winter.
 

Similar plumbing topics

Thanks for all the help. It was the gas valve...