Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Vert flue from a chimney stack in the Plumbing Jobs | The Job-board area at Plumbers Forums

Scott_D

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
6,128
I know I would need to check with MI's for boiler specific info -
But can anyone tell me the standard measurement for a vert flue from a chimney stack?
Is it 1500mm?
 
I know I would need to check with MI's for boiler specific info -
But can anyone tell me the standard measurement for a vert flue from a chimney stack?
Is it 1500mm?
I think 1500 was o/f Natural draught. But I was wrong before. What type off boiler are you going to fit there which boiler manufacturer?
 
500mm below or to the side but if the flue is higher than the outlet of the chimney then 1500
 
500mm below or to the side but if the flue is higher than the outlet of the chimney then 1500
Looking at Worcester MIs it's 500 from any structure, 600 from any balanced flue, 1500 from any open flue.
Does this mean 1500 from any chimney then?

The chimney belongs to next door (terraced house) so no way of telling if anything is still connected.
 
Looking at Worcester MIs it's 500 from any structure, 600 from any balanced flue, 1500 from any open flue.
Does this mean 1500 from any chimney then?

The chimney belongs to next door (terraced house) so no way of telling if anything is still connected.

Correct so if chi is higher than the flue 500mm away

But if flue is higher than chi 1500mm away required

And doesn't matter if it's got a fire or not unless your planning on capping it as they could not have one then in two years decide they want one making your install non compliant
 

Similar plumbing topics

A bit late but what were the test results, did...
Replies
10
Views
3K
I’ll make one, it’s basically only two bits of...
Replies
7
Views
859
If it’s in the manufacturer’s instructions...
Replies
1
Views
1K
Deleted member 120897
D
Yes it’s doable but I suspect it wouldn’t be...
Replies
1
Views
337
Atag let you go for the 600mm clearance away...
Replies
9
Views
861
Back
Top