Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Vibrating hot water return pipe from indirect cylinder in the Central Heating Forum area at Plumbers Forums

Messages
2
Hi,

I have two indirect water cylinders (Gledhill) connected to a gas boiler (Vaillant). The system is setup/programmed so that the tanks heat up twice a day for about 2 hours. When the tanks start to heat, one of them makes a loud vibrating noise, sometimes for about 15-20 mins, sometimes for longer. The noise seems to be coming from the hot water return pipe (i.e. the pipe taking the hot water back to the boiler). If I hold that pipe (it has insulating foam) tightly close to the cylinder then the noise stops.

This has been happening since we moved into the property about 9 months ago. I was worried that it's getting louder, but my wife thinks it's the same as it always was.

I was wondering if anyone can tell me ...
  • What is the likely cause?
  • How much do I need to worry? We're booked for a service in a couple of months anyway so could just get our plumber to look at it then, but do we need to get him out sooner?
Many thanks,
Antony
 
There have been numerous posts about these, have a look at this......

and

 
Too much flow through the return needs a lockshield gate valve fitting on the return from each cylinder 100% will fix the problem

Leave them fully open turn the boiler on to heat one up at a time and slowly close the lockshield gate valve until the vibration stops should be around 4-5 full turns etc
 

Similar plumbing topics

Recently over the past 2 months, the boiler or...
Replies
0
Views
3K
see same. below on this as some one has had...
Replies
1
Views
859
Sometimes the connection point of the cylinder...
Replies
3
Views
547
G
Could be one of a number. Need to know what...
Replies
1
Views
667
Back
Top