Viessmann 100-W System With Evohome | Central Heating Forum | Plumbers Forums
Guest viewing is limited

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Viessmann 100-W System With Evohome in the Central Heating Forum area at Plumbers Forums

IND_Nick

Esteemed
Gas Engineer
Messages
353
Morning,

I have a job later this week with the above , Viessmann Vitodens System boiler. It has a 4 pipe setup with internal diverter and at present there is a wireless thermostat/programmer controller in the hallway.
Customer wants a Honeywell Evohome System and I just wondered if I can wire this into the boiler to continue using the 4 pipe system and internal diverter, or do I need to pipe CH flow into a S Plan and just cap the DHW Flow/Return as I can only see 1 L and N available so assume this is for a 240v Heating control.
Any advice appreciated, thanks.
 
i like the 4 pipe I would use weather comp rather than evohome and fit the kit for hot water. But if the customer wants evohome. Rather defeats the object of the 4 pipe system doesn’t it.
 
Just spoke to Viessmann and they do a module that provides a 240v connection for the DHW so can all be wired up and remain with the 4 pipe setup.
The Evohome is because they work from home so want to zone the house, it's a semi that been extended on to extension heating pipes are a mess unfortunately as I'd normally recommend zoning for floors with weather compensation.
 

Similar plumbing topics

Thanks for the reply whats the best suggestion...
Replies
2
Views
1K
If the op has the newer colour display model...
Replies
5
Views
4K
Thanks for all above. I've done a few Evohomes...
Replies
5
Views
727
H
What system do you have? Can you post a photo...
Replies
1
Views
2K
Deleted member 120897
D
That is true - however with Vaillant...
Replies
4
Views
960
Back
Top