Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Viessmann capacitor missing in the Central Heating Forum area at Plumbers Forums

Messages
149
Just been to one of our installers jobs because customer said boiler wouldn't go off when the heating was turned off on the Hive. It's a heat only 100 series boiler. So I turn on the heating on the Hive and boiler comes on but when turned of boiler keeps running. I take off hive receiver from backplate and boiler goes off and 3 port closes to hot water. Put it back on and try Shaun to test when off my white of motorised valve is dead and all good but still 240 at switch live. But if I test between neutral and switch live the boiler shuts off. Strange. I've replaced the Hive so know it's not that. Could it be that the installer took out and through away the capacitor that should be between neutral and switch live #1
 
This part of your question:

Put it back on and try Shaun to test when off my white of motorised valve is dead and all good but still 240 at switch live. But if I test between neutral and switch live the boiler shuts off.

is incomprehensible to me. Maybe if you sketch a diagram you can refer to and also be explicit about what you mean by 'test' (voltage, current, resistance, jumper, etc.) I, or someone else, can help.

This may not be relevant but some of the most puzzling behaviours I've come across have been down to floating neutrals. There's been just enough capacitance between neutral and earth for low current devices to sort of work...

It seems unlikely that an installer would remove a component like a capacitor unless the they'd been told to, e.g. by the manufacturer's tech dept. IME, installers who've had any training at all know the importance of sticking to the MIs.
 
This part of your question:



is incomprehensible to me. Maybe if you sketch a diagram you can refer to and also be explicit about what you mean by 'test' (voltage, current, resistance, jumper, etc.) I, or someone else, can help.

This may not be relevant but some of the most puzzling behaviours I've come across have been down to floating neutrals. There's been just enough capacitance between neutral and earth for low current devices to sort of work...

It seems unlikely that an installer would remove a component like a capacitor unless the they'd been told to, e.g. by the manufacturer's tech dept. IME, installers who've had any training at all know the importance of sticking to the MIs.
It's ok. Gonna call Viessmann in the morning to find out so will update once I know
[automerge]1602711079[/automerge]
It's ok. Gonna call Viessmann in the morning to find out so will update once I know
Just found this. So yes the installer has removed as he told me this himself. Looks like its needed on the y plan system
 

Attachments

  • Screenshot_20201014-222836_Google.jpg
    Screenshot_20201014-222836_Google.jpg
    45.2 KB · Views: 23
Last edited:

Similar plumbing topics

This reminds me of the time I diagnosed a...
Replies
3
Views
989
I have a home with an oil boiler in a garage...
Replies
0
Views
637
Hello, I live in a two floor semi with a...
Replies
0
Views
764
Just a guess, but you may find that the...
Replies
5
Views
2K
It's not 'amateurish', what you've had...
Replies
3
Views
686
Back
Top