Hi All
Symptom : boiler locked out
I reset boiler and tried to restart calling for heating
sounds as though the fan is running but no ignition sequence
reset and tried calling for dhw
again sounds as though fan is running but still no ignition
reset again and removed vacuum pipe from fan and applied a bit of suction
to switch. ignition fired but stopped on removing suction
to me it sounded as though the fan is running (unless its just the motor) but on the outside of the fan casing is what loooks like a smaller
fan which isnt moving
are any of you guys familiar with this fan ?
is there known problems with these ?
cheers all
Derry